Non-motoring > Central Heating Timer Blowing Fuse Miscellaneous
Thread Author: zippy Replies: 7

 Central Heating Timer Blowing Fuse - RichardW
Unlikely the pump would blow the fuse even if it was stalled, and the valve shouldn't either, since it exists in the stalled state most of the time. Possibly a wire has come loose and fallen where it shouldn't or some water has got in where it shouldn't be! Have you got a multi meter? Can you access where the pump and valve were connected, you might be able to disconnect them one at a time to see if that stops the fuse blowing. Assuming this is a system with an external pump, then the boiler won't run for long without tripping on overheat if the pump is not running, but it could prove a point.
 Messages Author Date
 Central Heating Timer Blowing Fuse new zippy 21 Feb 21 23:53
 Central Heating Timer Blowing Fuse new RichardW 22 Feb 21 07:35
 Central Heating Timer Blowing Fuse new Zero 22 Feb 21 09:30
 Central Heating Timer Blowing Fuse new maltrap 22 Feb 21 10:23
 Central Heating Timer Blowing Fuse new percy 22 Feb 21 13:29
 Central Heating Timer Blowing Fuse new zippy 23 Feb 21 10:27
 Central Heating Timer Blowing Fuse new percy 23 Feb 21 14:21
 Central Heating Timer Blowing Fuse new maltrap 23 Feb 21 15:20