I think that probably the best solution is to turn the radial circuit with the 16A MCB into a 'ring' with a 30A mcb, by adding an extra 2.5mm cable from the consumer unit to the socket in the workroom. (This requires however that the existing cable run is in 2.5mm cable).
As an alternative, run an extension cable from a ring socket somewhere in the house for the use of the saw in the work room. It all depends on the geography of your situation.